Quote:It means it should put out a maximum of 125 amps for an hour. If you use all of the 1KW from the inverter this should be around 4 amps output if my calculations are correct (1000 watts / 240 volts = 4.16 amps). Which means your battery should last about 30 hours (125AH / 4 amps = 31.25). However this is seldom the case as there is a degree of redundancy involved so it's best to take off about 30%. Therefore your 125AH battery is really about 87.5AH (87.5AH / 4 amps = 21.875), so in reality it should last about 20 hours. One thing though is you shouldn't really completely discharge to battery and it should not be allowed to go down below about 30% before recharging, so taking taking that 30% off as well we have - 61.25AH / 4 amps = 15.31 hours, so you will need to recharge the battery after about 15 hours use at a maximum of 1 KW (4 amps).

LAC, your intentions are good but the calculation is way out. If you use 1kW power on a single 12v 125ah battery, you're looking at a very short time indeed.

Firstly, it's 1kW/12v = 83 amps! Not only will you have to use massive cables to carry the ampage (you could just get away with 16.0mm, depending, but I'd use 25.0mm personally).

Secondly, using 1kW, I reckon the battery would last you 3 mins max before you start endangering it's DOD life span.

Quite right, these batteries are designed for slow discharge and not an abrupt drain from huge loads.
I'm NOT political so DON'T correct me!
Reply


Messages In This Thread
Maplin deep cycle solar batteries - by Bonnox - 13 October 2013, 13:15
RE: Maplin deep cycle solar batteries - by Nix - 13 October 2013, 13:50
RE: Maplin deep cycle solar batteries - by Bonnox - 13 October 2013, 14:51
RE: Maplin deep cycle solar batteries - by Nix - 13 October 2013, 15:18
RE: Maplin deep cycle solar batteries - by Binnie - 14 October 2013, 06:11
RE: Maplin deep cycle solar batteries - by Nix - 14 October 2013, 08:51
RE: Maplin deep cycle solar batteries - by Binnie - 14 October 2013, 09:40
RE: Maplin deep cycle solar batteries - by Nix - 14 October 2013, 10:27
RE: Maplin deep cycle solar batteries - by Binnie - 14 October 2013, 11:30
RE: Maplin deep cycle solar batteries - by Nix - 1 November 2013, 21:00
RE: Maplin deep cycle solar batteries - by Skvez - 4 November 2013, 21:19
RE: Maplin deep cycle solar batteries - by Nix - 2 November 2013, 09:26
RE: Maplin deep cycle solar batteries - by Nix - 2 November 2013, 23:42
RE: Maplin deep cycle solar batteries - by Nix - 5 November 2013, 09:42
RE: Maplin deep cycle solar batteries - by Skvez - 5 November 2013, 12:08

Forum Jump:


Users browsing this thread: 1 Guest(s)